    Default Hitachi Seiki Seicos Sigma Alarms

    I need help in reseting these alarms 796 Battery Alarm,4th axis need zrn F300,4th axis battery zero F306, 4th axis battery down F307. I replaced all batteries. I know Fanuc controls well and I can not figure out how to reset these alarms no books. On Fanuc you go to p1815 and toggle APC to reset home.
    This is a TS15 Lathe Any help is great.

  2. #2
    Join Date
    May 2008
    Location
    Great State of Wisconsin
    Posts
    1,212
    Thanks
    7
    Thanked 134 Times in 112 Posts

    Default Re: Hitachi Seiki Seicos Sigma Alarms

    See if this will work for you.

    1. Black Screen Press ENTER
    2. You can see Screen Bottom: F1…F2…F3…F4…F5…
    3. Press F1 SEQUENCE Key
    4. Press F1 DIAGNOSE Key
    5. Press F5 NEXT Key
    6. Press F4 RESET Key
    7. Press “ SFT and ENTER at the Same Time

    Stevo
    (The opinions in this post are my own and not those of machinetoolhelp.com and its management)